30-400 Wiring of luminaires$ o/ Y2 m# l/ m. s
All electrical wiring on or within a luminaire shall be
9 z3 ^) i, f' R0 U' h+ A(a) neatly arranged without excess wiring;( R; T+ Q2 B: n
(b) not exposed to mechanical injury; and2 H& U3 D( e/ m8 Z% q) a
(c) arranged so that it is not subjected to temperatures above those for which it is rated.
6 z/ j5 r% X3 p$ N30-402 Colour coding
2 s6 f- w6 A* |1 ?Notwithstanding the requirements of Sections 0, 4, and 10 with regard to the colours used for distinguishing and identifying conductors, a continuous-coloured tracer in the braid of an individual braided conductor shall be permitted for the supply conductors of a luminaire, the colour of the tracer being black, white, and green for the ungrounded, identified, and bonding conductors respectively.
* Q2 Y( ]% s, x }30-404 Conductor insulation
# L# R8 F, Z' W/ m+ zLuminaires shall be wired with conductors at least No. 18 AWG, having insulation suitable for the voltage and temperatures to which the conductors may be subjected.* t! @ [9 _; T. K
30-408 Wiring of ceiling outlet boxes% a# S/ n7 B% l
(1) Branch circuit conductors having insulation suitable for 90 °C shall be used for wiring of ceiling outlet boxes on which a luminaire is mounted, except for boxes in wet locations where Type NMW or NMWU cables are used.
" l8 l( L* w% z+ \(2) For purposes of compliance with this Rule, the ampacity of 90 °C wire shall be limited to the ampacity of 60 °C wire. |
|