7 J  f" w; v0 u- K  b, ITwo  cutler –hammer advantage  starters are  doing the same thing:% p- D. c0 Y2 Z
After start 2-3 times, they will quit working, if you toggle the  start and stop buttons on DCS screen  , you will get another 2-3 running before they quit working again.
2 n) J' X2 ~; |+ t# V+ J7 N: aIt is a cycle.& C' d- l- W5 I& z+ b
8 i9 k: i6 j( U. o5 l8 U0 f
We isolate the network control and use the local start and stop only, the problem remains.
! j, x5 G% }$ P5 s5 vSwap one of the defective buckets with a good one, the new bucket works fine.; l: \' [) K* S' M( X
The problem should be inside the bucket.( j) v/ P# ^: x1 J

+ F) n# l7 @: P0 ^! O' BWhen the problem happened, we observed that  the contactor has a pulling action but will not seal.5 [$ V3 k. t4 H* M
Use a terminating screw divers to push in the contactor, it will not seal either.2 q$ J& D5 `, J" V) X8 X' U+ r2 S
Confirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we  bought two new control circuit boards and replaced the old ones, the problem is still the same.
) s5 q# _  O8 ~: V  w
) o; V; R2 {6 e! m3 nThe next thing we can think of  is the coil, we took the coil out to have a close look.8 K" o5 W6 ?" M- b: g' S
They  have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered  the connection and tried again.
- J( F; d* S3 }* Y" J8 g/ L It is getting better  this time, we have 7-8 times of running before it quit working. + ?$ J! X: o) H6 R- L  B
; {3 A" h/ n, i
The coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them.
1 O7 d4 \" N( P9 a/ a% d/ h  N" q4 s: ~! L" b+ O2 C
Do you guys have any input on this issue?
鲜花(1) 鸡蛋(0)
发表于 2010-3-26 17:07 | 显示全部楼层
有时候主接触点太脏,也会造成启动器无法正常工作
鲜花(0) 鸡蛋(0)
发表于 2010-3-26 17:37 | 显示全部楼层
本帖最后由 贾电工 于 2010-3-26 18:38 编辑
$ B8 H' E7 {8 U, f1 j
/ y1 _. I% E$ B% i* Y2 u8 K中国人在这里最好说中国话!说英语或想学英语请人到洋人论坛!
鲜花(7) 鸡蛋(0)
发表于 2010-3-26 17:42 | 显示全部楼层
老杨团队 追求完美
Don't know cutler –hammer advantage  starters very well, but had been worked on AB switch gears for a little while, which has two different coils, one to pull the vacum bottles up which employs larger current, another one uses less current to hold the connection---if the second coil fails, it won't be able to seal the connection.3 r# Z6 s; X' k. I& N. Q
Since your cutler -hammer works couple times,  I guess 侠客行 is right, or the sealing connection is just worn out.
鲜花(0) 鸡蛋(0)
 楼主| 发表于 2010-3-26 17:55 | 显示全部楼层
2# 侠客行 7 m: D3 N3 F9 o4 U
也想到这一点,不过这是新装的设备。
" M  e: C2 d$ x( C. X: _6 Y( l检查过触点没问题。