Two cutler –hammer advantage starters are doing the same thing:5 Y& ?9 s1 k& Q& D; o' e# U, M
After start 2-3 times, they will quit working, if you toggle the start and stop buttons on DCS screen , you will get another 2-3 running before they quit working again.
+ f2 i( K4 ~" x7 UIt is a cycle.$ ~* n: I3 p6 }* P
' Q; T4 u4 @1 \We isolate the network control and use the local start and stop only, the problem remains.# Y# Z* m* l8 s+ G7 m9 B
Swap one of the defective buckets with a good one, the new bucket works fine.) B7 ?4 `$ J D1 l F4 T- \- B
The problem should be inside the bucket.
8 ?9 B4 q) z8 f
) f# d9 B( o( O7 z9 _# }When the problem happened, we observed that the contactor has a pulling action but will not seal.
6 K* @! o/ V" lUse a terminating screw divers to push in the contactor, it will not seal either.1 I8 R+ x) O- G( Q+ d
Confirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we bought two new control circuit boards and replaced the old ones, the problem is still the same.5 b/ A* } d6 L2 T
1 C. ], P5 z6 P8 H( M! J1 l
The next thing we can think of is the coil, we took the coil out to have a close look.
, Q0 q: [/ t( [$ q$ G( W( ^They have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered the connection and tried again.6 v/ N1 b/ h% \# {
It is getting better this time, we have 7-8 times of running before it quit working. 4 N L3 ?2 {5 d
4 O& Q+ e, [2 Z
The coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them. ( I: c) ~$ j0 F* w. Y* R1 T. @" [
% u/ @* C4 y# {
Do you guys have any input on this issue? |
|