Two cutler –hammer advantage starters are doing the same thing:
! w9 J' E7 g% q9 ] After start 2-3 times, they will quit working, if you toggle the start and stop buttons on DCS screen , you will get another 2-3 running before they quit working again.
& B+ j! U% `. O5 Y: K0 HIt is a cycle.
- C! d7 Q& X0 m; q( J1 f, I' w! c& q8 A# k
We isolate the network control and use the local start and stop only, the problem remains.
" w) J; @# s! a4 wSwap one of the defective buckets with a good one, the new bucket works fine.* H9 g) F; q- a# g7 F# ~# A
The problem should be inside the bucket.+ y$ N) z6 v% ]* B1 N! M0 l
' X+ A" m3 U2 {& x. s8 _( oWhen the problem happened, we observed that the contactor has a pulling action but will not seal.
: O' [' r% y1 ]' J5 f8 KUse a terminating screw divers to push in the contactor, it will not seal either./ |& R5 M4 A! j+ q/ m( C
Confirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we bought two new control circuit boards and replaced the old ones, the problem is still the same.
) T0 \6 f/ b. ^1 t+ e, [6 K, |8 O( z! y$ M7 Z: X' n
The next thing we can think of is the coil, we took the coil out to have a close look.4 E9 A1 |, V3 @: @4 q3 A0 n. \
They have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered the connection and tried again.5 |: p; v2 n. U7 ^- `
It is getting better this time, we have 7-8 times of running before it quit working.
1 l' m _5 O+ F! c. @
. h9 M# [+ L9 M* s2 k& h; JThe coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them.
% T) t Q' Y+ E3 Z# ?8 [: S' o
, E8 h4 f: [8 R$ P: A( q6 |! Y& BDo you guys have any input on this issue? |
|