' h1 f/ ?; r7 a! _Two  cutler –hammer advantage  starters are  doing the same thing:, ~% E7 z$ r9 j
After start 2-3 times, they will quit working, if you toggle the  start and stop buttons on DCS screen  , you will get another 2-3 running before they quit working again.
$ o+ B' F- @0 c7 E2 pIt is a cycle.+ b; @, n$ k' Z) Y- |8 k; Y
3 q" A  _6 R' j8 G& o3 q. O# {
We isolate the network control and use the local start and stop only, the problem remains.* f7 }7 ~$ Y. K( u# d
Swap one of the defective buckets with a good one, the new bucket works fine.
5 ?* m2 a: t$ QThe problem should be inside the bucket.
: A3 d* Y- O- l% H$ C1 O
, l# }& X( [; \6 f( b: |1 hWhen the problem happened, we observed that  the contactor has a pulling action but will not seal.
" f( B& F( S9 P/ }2 r: m8 eUse a terminating screw divers to push in the contactor, it will not seal either.% q* F$ k: s3 d: R6 R
Confirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we  bought two new control circuit boards and replaced the old ones, the problem is still the same.
! ?6 t) S% A2 z' o0 k, b; Z6 ~
! K  `9 U0 c- a. h% m: _. y/ lThe next thing we can think of  is the coil, we took the coil out to have a close look.6 L1 c' T# H/ @
They  have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered  the connection and tried again.6 ^5 q9 b3 m3 m0 c: C/ l/ a( h
It is getting better  this time, we have 7-8 times of running before it quit working.
/ `/ D) i$ I8 P) p1 D3 u" W9 ?  [7 E6 D7 W4 X4 N
The coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them.
& o- @3 i: n9 k/ V$ O  f% @% i7 h* W: v" h& ^! L* f# V
Do you guys have any input on this issue?
鲜花(1) 鸡蛋(0)
发表于 2010-3-26 17:07 | 显示全部楼层
有时候主接触点太脏,也会造成启动器无法正常工作
鲜花(0) 鸡蛋(0)
发表于 2010-3-26 17:37 | 显示全部楼层
本帖最后由 贾电工 于 2010-3-26 18:38 编辑
) q3 t/ ]$ }* H9 k0 `+ H" X8 q/ g, u* n6 z
中国人在这里最好说中国话!说英语或想学英语请人到洋人论坛!
鲜花(7) 鸡蛋(0)
发表于 2010-3-26 17:42 | 显示全部楼层
老杨团队 追求完美
Don't know cutler –hammer advantage  starters very well, but had been worked on AB switch gears for a little while, which has two different coils, one to pull the vacum bottles up which employs larger current, another one uses less current to hold the connection---if the second coil fails, it won't be able to seal the connection.& k' ?" T. T9 D+ h( q7 H4 i# O
Since your cutler -hammer works couple times,  I guess 侠客行 is right, or the sealing connection is just worn out.
鲜花(0) 鸡蛋(0)
 楼主| 发表于 2010-3-26 17:55 | 显示全部楼层
2# 侠客行
! k7 M  F9 |, c也想到这一点,不过这是新装的设备。
; I* w3 I' e2 l0 P检查过触点没问题。