Two  cutler –hammer advantage  starters are  doing the same thing:# e4 n. w5 e# E6 T4 _0 g8 P; o
After start 2-3 times, they will quit working, if you toggle the  start and stop buttons on DCS screen  , you will get another 2-3 running before they quit working again.
+ q% C6 D! K% M6 y  e! WIt is a cycle.
. c: n3 w- b7 b; {) }* n4 q) J. x2 o3 \4 o! M  {
We isolate the network control and use the local start and stop only, the problem remains.
& P3 t* I3 @3 ^- R0 hSwap one of the defective buckets with a good one, the new bucket works fine.
3 O2 o3 z( Q; \, |* Z9 G. JThe problem should be inside the bucket.1 }9 G# G9 }- Y/ E4 c

! d3 c% e" ~' s5 `/ v) bWhen the problem happened, we observed that  the contactor has a pulling action but will not seal.$ I" F+ E7 D, }6 F, p$ ~9 R
Use a terminating screw divers to push in the contactor, it will not seal either.6 B# k( L$ [0 K
Confirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we  bought two new control circuit boards and replaced the old ones, the problem is still the same.
* }& ?( X4 [- N1 j6 j9 V; N, d
7 S2 _- d  \+ J; \1 M& E7 y8 kThe next thing we can think of  is the coil, we took the coil out to have a close look.  D: Z$ N4 v2 x2 v, k
They  have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered  the connection and tried again.$ O: c) _0 T0 ~# _/ B0 C
It is getting better  this time, we have 7-8 times of running before it quit working. ! t4 {1 R0 j+ ?/ W0 S( X4 a  z5 X
0 m) C! g+ k' D" m2 `7 [
The coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them.
1 M3 z/ V$ y& D6 h+ E
3 T, }7 Q  ~! H+ w6 D* dDo you guys have any input on this issue?
鲜花(1) 鸡蛋(0)
发表于 2010-3-26 17:07 | 显示全部楼层
有时候主接触点太脏,也会造成启动器无法正常工作
鲜花(0) 鸡蛋(0)
发表于 2010-3-26 17:37 | 显示全部楼层
本帖最后由 贾电工 于 2010-3-26 18:38 编辑 " U" b9 c8 z, q

" ^. w8 Y& `: l- e1 ]中国人在这里最好说中国话!说英语或想学英语请人到洋人论坛!
鲜花(7) 鸡蛋(0)
发表于 2010-3-26 17:42 | 显示全部楼层
老杨团队 追求完美
Don't know cutler –hammer advantage  starters very well, but had been worked on AB switch gears for a little while, which has two different coils, one to pull the vacum bottles up which employs larger current, another one uses less current to hold the connection---if the second coil fails, it won't be able to seal the connection.
) e) G7 T# R" t+ I9 }Since your cutler -hammer works couple times,  I guess 侠客行 is right, or the sealing connection is just worn out.
鲜花(0) 鸡蛋(0)
 楼主| 发表于 2010-3-26 17:55 | 显示全部楼层
2# 侠客行
  L1 Y, C$ i( F8 b也想到这一点,不过这是新装的设备。
& \- l( b* t! O, ~, i# R检查过触点没问题。