: `1 n4 q$ i; N/ \$ T$ e5 L" w! f) sTwo cutler –hammer advantage starters are doing the same thing:% A! [4 Y* E' ^ }8 l3 l/ W
After start 2-3 times, they will quit working, if you toggle the start and stop buttons on DCS screen , you will get another 2-3 running before they quit working again. , X3 K1 e7 v/ [& y- n) a6 B
It is a cycle.) w% k4 p$ ~' L" l- C% i
9 u; h, |. b z- F, d
We isolate the network control and use the local start and stop only, the problem remains.7 p! I5 |: U0 U v, f5 C
Swap one of the defective buckets with a good one, the new bucket works fine. k5 q$ Z' p, h
The problem should be inside the bucket.
Y' C! T$ G' H1 c- p# S6 @
; q o7 }% t( h, g8 tWhen the problem happened, we observed that the contactor has a pulling action but will not seal.
+ n" I. z! U [$ `. m0 f, F0 f, XUse a terminating screw divers to push in the contactor, it will not seal either.- @0 l) l2 O2 x% b$ @7 L# o
Confirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we bought two new control circuit boards and replaced the old ones, the problem is still the same.- g, h8 ^# T$ b: c; J, T
, y) m7 z* X; Q3 t \The next thing we can think of is the coil, we took the coil out to have a close look.
" O- {+ Y! k' I. LThey have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered the connection and tried again.+ B& @! l7 D$ m; E& b' r
It is getting better this time, we have 7-8 times of running before it quit working. + x' r, V# G% r6 q, s# [& M# i
; {. ]# W; o7 w3 F, T6 ^! k$ \& `
The coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them. + X2 P$ |1 E3 k, v. u
, _" n# w. P) p, c
Do you guys have any input on this issue? |
|