足球看完了来看看题目。6 b) {, o# X2 p) I1 C) \2 ^
- }& k/ Y. U% @4 c: E
The length of the heat trace is 22 meters. The size of the heat trace is 5/16 inch (WATTS/ m SUPPLIIED is 43.7)
( G% p4 F2 K' U" p+ E& D2 HThe drawing is shown as figure 1. (All data is from the memory. They are not the same as the real drawing, but a little bit different)" V) ]5 {$ W) X$ \/ K% f
We can see it is not easy to install the 22 meters heat trace according as figure 1
( G/ N7 U; O d$ O2 }4 f4 H- A4 X, G5 J* Y$ D' K
! a3 C- ~. s0 b8 x8 X6 e' C% _% y: s& N+ n
3 u9 T% r: U9 L3 UAs a normal question we just discuss:
8 T% H6 d A# Z& j3 T" MHow do you run these 9.4 meters heat trace (size 5/16 inch) on the 3 inches 1.4 meters pipe ? 9 k' {0 S5 s& }+ d- @- ]
I call this is JACK LAI Spiral Method 螺旋法3 Q* O0 v. ?% ?
The outside circumference of the 3 inch pipe is more than 10 inches. See figure 2.( g# q! R8 [( L$ j/ L) t g4 ~0 T
There are 10 positions to plac the heat trace. They are 0.1,2,3,,,,,9. The distance between each position--heat trace is about one inch. 9 @8 T5 h+ T6 k
Because the pipe is horizontal, position 0 can not be placed. See figure 2
: M# k& H: z3 YBecause the maximum bend radius of the heat trace is 2 inches( see note 1), position 5 can not be placed. See figure 2. Then the route of the heat trace can be like figure 3+ D+ W8 h4 Q8 n. L7 G! Q* L
The total heat trace that can be installed here is about
7 [) L1 H) I% M. Y/ D1.4 * 6 + 1 * 2 = 8.6 + 2 =10.8 Meters. I. Y8 @1 D0 k$ n8 D
So, the 9.4 meters heat trace can be installed along the 3 inched 1.4 meters pipe without a problem. ( W8 B( P- y& o+ ?: k6 {
) s8 T5 R' l6 ?& j9 V) A
Note :
/ }9 V. A4 t4 P/ `6 Y# R# D3 O1. The minimum bend radius:% ?9 [* P. k- v9 i
Because the heat trace size here is 5/16, 6 times the outside diameter of the heat trace is; p+ z, l% o0 l# O9 ]$ ]
5/16 *6 = 30/16 almost = 2 inches, ]5 c, z' N# ]6 Q- [) z2 P: X
So the maximum bend radius is 2 inches." {5 E9 k0 h0 P# W. d( p- \. N( S
: i2 U% {; D9 t( _6 Q/ T8 d2 V
- H" S& z/ _2 ?
3 g# A e$ V7 ~! k0 `3 n8 Y6 ^8 a9 WSummary# X3 _8 F( L" c
As regular ! H1 I5 _% }& d' z' R, K+ X
For 3 inch pip: If heat trace size is 5/16 inch, and no RTD, the box position is close to the end of pipe. 1 meter long pipe
7 w. k, G! u; n2 M X2 n) U" hif the pipe is horizontal, The length of heat trace can be installed is about0 k* u2 g+ F N6 g6 o
1 * 9 = 9 meters
4 G0 R+ E* X4 aIf the pipe is vertical, The length of heat trace can be installed is about
& f' C# h4 |! n _4 b1 * 10 = 10 meters. # f# w, E( R7 T# K, S
For 2 inch pipe: If heat trace size is 5/16 inch, and no RTD, the box position is close to the end of pipe. 1 meter long pipe
/ T4 e6 e% }. D3 w% s8 S0 C; ^2 ~if the pipe is horizontal , The length of heat trace can be installed is about
: d5 r! R4 M' L0 M1 * 4 = 4 meters, d! x$ s$ S( L b; N3 w4 R
If the pipe is vertical, The length of heat trace can be installed is about
- T6 l- b% a% p+ Q" X$ o/ w! o1 * 5 = 5 meters. |
|