7 F. F: g% V$ Q2 Q3 hTwo cutler –hammer advantage starters are doing the same thing:5 c T) f1 y* U
After start 2-3 times, they will quit working, if you toggle the start and stop buttons on DCS screen , you will get another 2-3 running before they quit working again.
% ?9 W5 F5 b" Y, IIt is a cycle.& O7 W) r7 \, C" g( ?+ q5 m# }
6 ]8 k: a" d, M3 C; x6 K
We isolate the network control and use the local start and stop only, the problem remains.
: q2 u1 ^0 v' I, BSwap one of the defective buckets with a good one, the new bucket works fine.
. ]0 v5 |# o/ Z; _! RThe problem should be inside the bucket.# e9 W2 w7 t& Y. K
9 b3 @2 _3 l/ w! sWhen the problem happened, we observed that the contactor has a pulling action but will not seal.
: T* P5 _, w6 Z0 J" ?; TUse a terminating screw divers to push in the contactor, it will not seal either.* n. q% u# c( t9 b
Confirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we bought two new control circuit boards and replaced the old ones, the problem is still the same.
2 A q' N1 \1 P+ F, k# O8 x
# [ Y) Z: |) H5 _+ p- AThe next thing we can think of is the coil, we took the coil out to have a close look. D$ C2 c7 I f. [
They have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered the connection and tried again.
4 g0 |! E- B2 | It is getting better this time, we have 7-8 times of running before it quit working.
* z5 { h' I6 _3 x( x1 d
6 l$ E6 t% I6 p0 ^& D' X* PThe coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them. 7 V, r' F8 p q
. k i z9 W u+ [) `' cDo you guys have any input on this issue? |
|