Two cutler –hammer advantage starters are doing the same thing:
# _$ W! N) c7 r" ` After start 2-3 times, they will quit working, if you toggle the start and stop buttons on DCS screen , you will get another 2-3 running before they quit working again.
7 Z& W9 y# u" }0 n# `; UIt is a cycle./ q/ G! U4 F( L( ~$ o8 s
& A1 H) N' L! s1 X
We isolate the network control and use the local start and stop only, the problem remains.
* C7 t9 o9 F7 \+ n, a' h1 y- R2 gSwap one of the defective buckets with a good one, the new bucket works fine.* \) h5 f! l) |7 o" F. \+ v& E
The problem should be inside the bucket.' Y6 M7 c# Z7 J% o! n. n
* a+ I& M9 F; b4 W! x5 Z: \
When the problem happened, we observed that the contactor has a pulling action but will not seal.
7 _/ j' R7 @1 m+ u a: _- O3 bUse a terminating screw divers to push in the contactor, it will not seal either.
0 u: S6 s* F4 o" U+ h- {Confirm with TECH support this should be a problem with the control circuit board inside the advantage starter, we bought two new control circuit boards and replaced the old ones, the problem is still the same.# b& [; n, e: K- L. L
/ ~. K9 A# A9 o0 Y8 p3 P5 y! @
The next thing we can think of is the coil, we took the coil out to have a close look.) A7 |# j( r- n; ?( }! y9 d+ M; m
They have a fork to pinch inside the two leads to make connection, it is not a good design at all. We soldered the connection and tried again.; X/ ^7 x, e& Q8 h- E
It is getting better this time, we have 7-8 times of running before it quit working. 3 y5 c! p$ e4 m! U# w
u9 P2 l' C- a; `
The coil should be the problem, we ordered two of them. But it will take 5-6 weeks for us to get them. % ~- R) L1 @2 n6 O
^* ^( i4 Q c1 p, p* ?Do you guys have any input on this issue? |
|